I have a client who wants to change the use of an existing 5" slab on grade to be used as the floor for a "warehouse" that was previous office space.
I've asked for what type of forklift he intended on using and if there were racks to be used in the warehouse.
The plans state the SOG=
5" concrete sog with #4 @ 48 ew and 6x6-W1.4x1.4 wwf on a granular 4" fill
f'c = 3000 psi
Using ACI 360-06 COE curve A3.1
flexural strength = 411psi
I assumed a modulus of subgrade reaction of 100, but even if I say its 200 then the charts say Design Index I...4000# capacity...design axle load of 10000#
Does that sound right? Do you think I should have them core the slab to make sure it's 5" thick and then check the subsurface as well?
How do you know what the weight/reactions on a rack system will be?
Thanks!