Is there a standard on maximum allowable installed interior and exterior lighting power for substations in Canada?

 
Replies continue below

Recommended for you

I can think of two reasons to limit the maximum - There may be energy conservation laws that set limits, and for exterior there may be local laws about maximum nighttime light levels or light spillover to adjacent property.

Alan
“The engineer's first problem in any design situation is to discover what the problem really is.” Unk.
 
I am looking for required watt/sqrm values for substation lighting designs. Inside the control room and outside the subsation. As "undervoltage" suggested, I may need to refer to IES hanbook,
Undervoltage: What book title refers to this specific subject?
Thank you.
 
NESC Table 111-1 gives required illumination levels for electric supply stations in the USA. Is there a similar code for utilities in Canada?
 