JKW05
Structural
- May 23, 2005
- 251
Say we're fastening a nominal 2x member to another nominal 2x member with lag screws.
2015 NDS 12.1.4.6: "The minimum length of lag screw penetration, pmin, not including the length of the tapered tip, E, of the lag screw into the main member of single shear connections ... shall be 4D."
If a lag screw length is selected such that the full length of the tapered tip projects through the far side of the main member, then we would have a full 1-1/2" of penetration into the main member. But based on the 4D requirement it appears that the maximum allowable lag screw size is 3/8" diameter (4 * 3/8 = 1-1/2"). Additionally, a 50% reduction of the values in Table 12J would be required (p/8D = 1.5/(8*.375) = 0.5).
1.) Therefore, 1/2" lag screws are not permitted to be used for this condition. Is this a correct interpretation?
2.) 12.1.4.6 specifically uses D in the 4D requirement. Could a case be made for using the root diameter (Dr) to determine the 4D requirement?
Thanks for your input.
JKW
2015 NDS 12.1.4.6: "The minimum length of lag screw penetration, pmin, not including the length of the tapered tip, E, of the lag screw into the main member of single shear connections ... shall be 4D."
If a lag screw length is selected such that the full length of the tapered tip projects through the far side of the main member, then we would have a full 1-1/2" of penetration into the main member. But based on the 4D requirement it appears that the maximum allowable lag screw size is 3/8" diameter (4 * 3/8 = 1-1/2"). Additionally, a 50% reduction of the values in Table 12J would be required (p/8D = 1.5/(8*.375) = 0.5).
1.) Therefore, 1/2" lag screws are not permitted to be used for this condition. Is this a correct interpretation?
2.) 12.1.4.6 specifically uses D in the 4D requirement. Could a case be made for using the root diameter (Dr) to determine the 4D requirement?
Thanks for your input.
JKW