i agreed with voyageofdiscovery said the maximum spacing is uneconomical design,
Voi :
1. what is the formula that you use to calculation group piles to get efficiency group factor (coverse labare, vesic, or..)
2. can you share the layout of group pile and working load on single pile and also working load will be supported by pile group?
generaly, if spacing pile to pile (centre-centre) more than 3 times of pile perimeter, group reduction factors need not be applied,
i.e : Pile Dia = 3ft, -> 3 x pi() x 3ft = 28 ft --> no need to applied reduction factor. (source: code of practice for foundation_2004_HK)
[CMMIW]
this indicate no maximum spacing pile in pile group, if the spacing more than 3 times pile perimeter the group pile axial capacity is sum of axial single pile.
M.A.