Maxpak

Status
Not open for further replies.

fatjonnie

Mechanical
Mar 16, 2012
4
I am trying to regulate the speed, and torque settings for a MaxPak III with a PLC. These were origionally controlled by speed pots.

The problem lies with the fact that the drive uses 0-15 Vdc as its control voltage. My signal conditioner is 0-10 Vdc. Has anyone run into this before?
 
Replies continue below

Recommended for you

Thanks for the quick response, that looks like it would do the trick. This would scale the output to the range I am looking for. Would I have to use two of these units to achieve regulation from my 0-10 Vdc isolated signal conditioner.

The way I have it in my head is that I would need to take the 15v from the drive, bring it to 10 Vdc. Then run it through my signal conditioner. Then take the 0-10 vdc from the signal conditioner and rescale it to a 0-15v output back to the drive.

Am I missing something obvious?
 
It doesn't look like you're missing anything, but I don't know the particulars of your signal conditioner or the control loop.



Good on ya,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies
 
Can't you just scale the input?

(For a 1725 type application) Seems like you should be able to set something like 15V = 2585RPM so at 10V you have 1725RPM.

Or am I missing the whole point?

Keith Cress