I HAVE A 63 MCB IN A MAIN PB IN GROUND FLOOR IS FEEDING A 63 MCCB IN A FIRST FLOOR ITS A VILLA AND BOTH ARE 3P.
MY QUES IS CAN A MCB FEEDS A MCCB OF? AND IF IT CAN WHAT ARE THE CONDITIONS NEEDED TO BE DONE AND IS THERE IS ANY ARTICLE ABOUT THAT IN NEC OR IEC PLZ INFORM ME
 
Replies continue below

Recommended for you

As posted in thread240-317941,

It can, but why would you want to? Waste of money, and you won't get any benefit of the higher performance of the 63A MCCB.

Is the CAPS lock on your computer broken? Either buy a new keyboard or stop posting until you fix it. [smile]


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
The difference is that, compared to an MCCB, if there is a fault in the circuit the MCB has a MUCH lower capacity to withstand the physical forces created by the fault current flow without blowing up and becoming shrapnel. Most MCBs are not rated for more than 10,000A (10kA) interrupt capacity, many MCCBs are good for up to 65kA, some even to 100kA. So consequently an MCCB will cost a LOT more money and take up a lot more room, it has to.

But if your system from the utility has an Available Fault Current (AFC) that is lower than 10kA (or whatever) rating of the MCB, then the MCB will be OK. If that is the case, then as Scotty said, someone wasted money buying an MCCB to go down stream from it, an MCCB will always have a higher IC rating than an MCB. The interrupt capacity in the circuit however is only as good as the weakest link, in this case the MCB.

If on the other had the AFC is greater than whatever the MCB is rated for and someone in the past replaced an MCCB with it, as I might expect, then that will be a dangerous violation of whatever codes are enforceable in your neck of the woods. It bears some serious attention to detail.

In either case you will not find a publication telling you what you want to hear, because apart from the waste of money, there is no rule against having a device that is seriously overqualified for the task at hand. So if like I said, the AFC is below the interrupt capacity rating of the MCB, then there is nothing inherently wrong with having the MCCB down stream of it.

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)

For the best use of Eng-Tips, please click here -> faq731-376
 
George, those tables all assume the MCCB is the upstream device. I can't find any information relating to the situation where the MCCB is the downstream device. It isn't surprising because no one would intentionally design a system with an MCB protecting an MCCB.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 