What does "exposed" mean in the phrase "exposed members"? How would you convince the AHJ that's what it means?
In NFPA 13 2013, Table 8.6.2.2.1(a) has many interesting things going on...
A short snippet from the handbook giving us additional info:
If you look at the table where it says "Combustible unobstructed with no exposed members" under "Construction Type", I want to ask how this is possible to be constructed?
A couple of senior sprinkler nicet IV's have given me the interpretation that "exposed members" means "combustible members" such as wood. So having rigid metal frames or steel bar joists would not be counted as "exposed members", meaning this "Combustible unobstructed with no exposed members" type of construction is entirely practical and common.
However, if you interpret it literally, "exposed members" does not say "combustible members" and I would say it would literally apply to any member - including steel ones. But then the question is, is it even possible to construct a large-area roof without exposed members? If not, obviously there is more here than just the literal interpretation.
What does "exposed" mean in the phrase "exposed members"? How would you convince the AHJ that's what it means?
In NFPA 13 2013, Table 8.6.2.2.1(a) has many interesting things going on...
A short snippet from the handbook giving us additional info:
If you look at the table where it says "Combustible unobstructed with no exposed members" under "Construction Type", I want to ask how this is possible to be constructed?
A couple of senior sprinkler nicet IV's have given me the interpretation that "exposed members" means "combustible members" such as wood. So having rigid metal frames or steel bar joists would not be counted as "exposed members", meaning this "Combustible unobstructed with no exposed members" type of construction is entirely practical and common.
However, if you interpret it literally, "exposed members" does not say "combustible members" and I would say it would literally apply to any member - including steel ones. But then the question is, is it even possible to construct a large-area roof without exposed members? If not, obviously there is more here than just the literal interpretation.
What does "exposed" mean in the phrase "exposed members"? How would you convince the AHJ that's what it means?