freefallingbody
Electrical
- Aug 18, 2003
- 55
Hi,
I have a 25 mWC, 510 m3/h rated pump directly coupled with 60 HP, 1470 rpm motor pumping water in a cooling tower circuit.
I wanted to measure the flow of this pump. I used a transit time type ultrasonic flow meter and got a flow of 520 m3/h. Since I don't trust these ultrasonic meters, I wanted to cross check the flow by another method. Since this is a new pump, I thought of cross checking the flow by measuring diffential pressure and refering to performance curves.
I measured the differential pressure across the pump. It was found to be 24 mWC. From the performance curve of the pump, corresponding to the head of 24 meters, the flow is around 525 m3/h. Both flow measurement and estimation are thus very close. I was very happy.
...But then I found out that the power input to the motor is only 32 kW. This would theoretically make the pump more than 100% efficient. I was expecting a motor power consumption of 43 to 45 kW based on the pump performance curves.
Any thoughts on what to do next, to decide on the flow?
(I even went to the extent that I switched off the pump from the main electical panel to ensure that I am measuring the power input to this pump only!)
Thanks in advance.
Dinesh
I have a 25 mWC, 510 m3/h rated pump directly coupled with 60 HP, 1470 rpm motor pumping water in a cooling tower circuit.
I wanted to measure the flow of this pump. I used a transit time type ultrasonic flow meter and got a flow of 520 m3/h. Since I don't trust these ultrasonic meters, I wanted to cross check the flow by another method. Since this is a new pump, I thought of cross checking the flow by measuring diffential pressure and refering to performance curves.
I measured the differential pressure across the pump. It was found to be 24 mWC. From the performance curve of the pump, corresponding to the head of 24 meters, the flow is around 525 m3/h. Both flow measurement and estimation are thus very close. I was very happy.
...But then I found out that the power input to the motor is only 32 kW. This would theoretically make the pump more than 100% efficient. I was expecting a motor power consumption of 43 to 45 kW based on the pump performance curves.
Any thoughts on what to do next, to decide on the flow?
(I even went to the extent that I switched off the pump from the main electical panel to ensure that I am measuring the power input to this pump only!)
Thanks in advance.
Dinesh