- May 27, 2015
- 3
I am reviewing a not quite typical ledger masonry wall connection. The masonry wall has an angle bolted to it, with anchors at 24" on center. The vertical angle leg sits flush with the face of the 10" masonry wall. The horizontal leg supports steel joists. In designing the masonry wall, I have always measured eccentricity from the center of the wall to the bearing point of the joists. The connection I am reviewing implies that the angle internally resolves the eccentricity from the center of bearing to the back of the angle/face of wall. Then the masonry wall only sees the eccentricity from the gravity loads applied at the back face of the angle. Naturally, this reduces the eccentricity on the wall from 7.5" to 5.5", a considerable amount. This original design was performed by a well known company, so before I call them out, I was hoping for some help finding code references.
I've looked through several and only find 'use "e" to apply the moment induced by gravity loads' and no code backup for the measurement of "e".
Thanks for guidance or new places to look.
I've looked through several and only find 'use "e" to apply the moment induced by gravity loads' and no code backup for the measurement of "e".
Thanks for guidance or new places to look.