Hi,
If i measure harmonic, the best is to measure it directly to the drive (on the power cable or bus), but if i can't, do i'll lost a lot of data if the power analyser is connected to CT and PT?
I was thinking, if the PT is connected in Delta, i'll probably lost a lot of 3rd harmonic?
So i want to know if it's acceptable to measure it that way or not, and if there's a standard to refer at. Do the standard IEC 61000-4-7 is very usefull and do i must buy it absolutely or not? I must measure untill the 50th harmonic and it's the harmonic current which are important for this case.
Thanks