I found myself in a debate with someone and perhaps both of us have a point, maybe we see things differently. Hence, I would like to obtain other's comments.
On a reversing starter control, there are two contactors wherein interlocks will must be included to prevent both contactors CLOSING simultaneously. I do understand the electrical interlocks wherein the auxiliary contact of each contactors will be wired to prevent energizing one contactor coil if the other contactor coil is currently energized.
The confusion lies on the momentary pushbuttons (FWD and REV) pushbuttons (see attached diagram). I see this momentary pushbuttons still FUNCTION as an ELECTRICAL INTERLOCK because their contacts are still electrically wired and operate to block or prevent energizing one coil. Although both pushbuttons are mechanically operated, their associated contacts still function as an "electrical interlock". The only mechanical interlock I would consider is the part where both pushbutton contacts are MECHANICALLY INTERLOCKED WITH EACH OTHER.
My friend's opinion is that since both pushbuttons are actuated by mechanical means (finger-pushed), they are mechanical interlock (which I disagree).
Mechanical interlock to me is non-electrical operation and there are no wiring like in the case of "kirk key" applications or an ABB VM5 which have insulated mechanical linkage to block the operating mechanism of a contactor.
Your opinion is highly appreciated.
Thanks you.
On a reversing starter control, there are two contactors wherein interlocks will must be included to prevent both contactors CLOSING simultaneously. I do understand the electrical interlocks wherein the auxiliary contact of each contactors will be wired to prevent energizing one contactor coil if the other contactor coil is currently energized.
The confusion lies on the momentary pushbuttons (FWD and REV) pushbuttons (see attached diagram). I see this momentary pushbuttons still FUNCTION as an ELECTRICAL INTERLOCK because their contacts are still electrically wired and operate to block or prevent energizing one coil. Although both pushbuttons are mechanically operated, their associated contacts still function as an "electrical interlock". The only mechanical interlock I would consider is the part where both pushbutton contacts are MECHANICALLY INTERLOCKED WITH EACH OTHER.
My friend's opinion is that since both pushbuttons are actuated by mechanical means (finger-pushed), they are mechanical interlock (which I disagree).
Mechanical interlock to me is non-electrical operation and there are no wiring like in the case of "kirk key" applications or an ABB VM5 which have insulated mechanical linkage to block the operating mechanism of a contactor.
Your opinion is highly appreciated.