I am working on renovations to a High School machine shop which involves relocating the shop from one room to another. The idea is to reuse equipment where possible.
The existing shop has rotating machines fed from a panelboard which is fed from a lighting contactor. The coil of the contactor is wired to 3 emergency stop push buttons around the room so that the activation of any of the 3 buttons will open the contactor, killing power to all the machines. In the existing system, the contactor is of the mechanically-held type: the e-stops open the contactor, a keyed momentary-action switch recloses it.
My problem with this system is that in the event of a power outage with the contactor in the normally-operating closed state, when power is restored many of the machines will come on automatically. A few of the machines have contactors built in, others latch on/off. I feel this presents an infrequent but serious hazard (keep in mind we're talking about a high-school environment).
I see three options:
1) Status quo. Warn the shop instructor about restart.
2) Replace the existing contactor with a (fail-open) electrically-held contactor (complete with a momentary-action start/reset switch and seal-in contact).
3) Add local contactors with start/stop momentary-action PBs to machines which don't already have them.
I have been advised by a senior PEng (I am an E.I.T) that the existing equipment is sufficient and the budget is small (contactor replacement would be 5-10% of electrical construction budget). There's politics involved, but I would like to have some second opinions on what is the best engineering solution.
Your comments would be greatly appreciated.
The existing shop has rotating machines fed from a panelboard which is fed from a lighting contactor. The coil of the contactor is wired to 3 emergency stop push buttons around the room so that the activation of any of the 3 buttons will open the contactor, killing power to all the machines. In the existing system, the contactor is of the mechanically-held type: the e-stops open the contactor, a keyed momentary-action switch recloses it.
My problem with this system is that in the event of a power outage with the contactor in the normally-operating closed state, when power is restored many of the machines will come on automatically. A few of the machines have contactors built in, others latch on/off. I feel this presents an infrequent but serious hazard (keep in mind we're talking about a high-school environment).
I see three options:
1) Status quo. Warn the shop instructor about restart.
2) Replace the existing contactor with a (fail-open) electrically-held contactor (complete with a momentary-action start/reset switch and seal-in contact).
3) Add local contactors with start/stop momentary-action PBs to machines which don't already have them.
I have been advised by a senior PEng (I am an E.I.T) that the existing equipment is sufficient and the budget is small (contactor replacement would be 5-10% of electrical construction budget). There's politics involved, but I would like to have some second opinions on what is the best engineering solution.
Your comments would be greatly appreciated.