Have an interesting problem and trying to think outside the box.
Working in a hospital doing a replacement of about 100 old chilled water fan coils with new, but with the addition of hot water heat. These serve medical offices only, no patient rooms. They were installed 20-40 years ago and are pretty much beyond their functional life. Unfortunately, when they were installed there was no outside air provided. Some (maybe half) had openable windows, but the other do/did not. So I need to get OA to the units (around 50) without openable windows.
Also unfortunaely, there is no reasonable menas to get OA to these units.
a. Corridor ceilings are packed. A 2" pipe may be able to be installed, but no way an OA duct.
b. Most of the problem rooms are interior spaces, so no exterior wall.
c. No room in corridor to duct OA across to get to an exterior wall.
d. The only option is to create an OA fan room in the basement, run OA duct horizontally around 400 liner feet, then branch off into OA risers appx 12 times, and come through 3 floors of occupied space to get to our floor with the OA risers. IMHO this is unreasonable, and will be extremely expensive.
e. Could also go up and do the same thing from the roof, but would have the same issues of risers through 3 floor of occupied space.
Had another idea this weekend when out in the garage working on stuff. Why not use the Medical Air system to provide OA? I can easily get 100 cfm through a 1.5" pipe. Expensive? Yes, but not compared to a new ducted system in the basement, risers, coring holes, fire dampers, furring out shafts, etc. I believe this is actually a "relatively" economical solution.
Other than apparantly never having been done before (at least according to my googling), does anyone see any downsides other than cost? This would be off of an existing oversize bonafide Medical Air system, with testing and alarms, so I am not worried about quantity or quality of air.
And no, this is not a late April Fools joke...
Working in a hospital doing a replacement of about 100 old chilled water fan coils with new, but with the addition of hot water heat. These serve medical offices only, no patient rooms. They were installed 20-40 years ago and are pretty much beyond their functional life. Unfortunately, when they were installed there was no outside air provided. Some (maybe half) had openable windows, but the other do/did not. So I need to get OA to the units (around 50) without openable windows.
Also unfortunaely, there is no reasonable menas to get OA to these units.
a. Corridor ceilings are packed. A 2" pipe may be able to be installed, but no way an OA duct.
b. Most of the problem rooms are interior spaces, so no exterior wall.
c. No room in corridor to duct OA across to get to an exterior wall.
d. The only option is to create an OA fan room in the basement, run OA duct horizontally around 400 liner feet, then branch off into OA risers appx 12 times, and come through 3 floors of occupied space to get to our floor with the OA risers. IMHO this is unreasonable, and will be extremely expensive.
e. Could also go up and do the same thing from the roof, but would have the same issues of risers through 3 floor of occupied space.
Had another idea this weekend when out in the garage working on stuff. Why not use the Medical Air system to provide OA? I can easily get 100 cfm through a 1.5" pipe. Expensive? Yes, but not compared to a new ducted system in the basement, risers, coring holes, fire dampers, furring out shafts, etc. I believe this is actually a "relatively" economical solution.
Other than apparantly never having been done before (at least according to my googling), does anyone see any downsides other than cost? This would be off of an existing oversize bonafide Medical Air system, with testing and alarms, so I am not worried about quantity or quality of air.
And no, this is not a late April Fools joke...