Hello All,
My application involves a 5 MVA 27.6 kv/4.16 kV Primary Delta and Secondary is star solidly grounded transformer. A 4.16 kV switchgear is fed from the secondary and I have been told by my utility standard guys that the practice of connecting outgoing feeder cables is as following:
1. X0(neutral) bushing connection of solidly grounded tranformer is not brough in to the switchgear building. It is connected throught a bare copper wire to through ground grid and a 600 V insulated cable is taken outside the street pole for the outgoing three phase 4 wire feeders.
2. 4 kv switchgear has a 1/2"x2" ground bus running bus within. Switchgear has three outgoing feeders, each cable is a single conductor 500 MCM with concentric neutral(3X 1C, 500 MCM).Swgr is 2000 A with each outgoing feeder with a 1200 A breaker.
Here is my question, Is it acceptable to connect concentric neutral for each feeder to the ground bus with in the switchgear. I have attached a picture. COuld you please suggest, if what is scientfically correct way to do things or I have it right.