Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Medium Voltage Switchgear 3

Status
Not open for further replies.

PoliPoliCarps

Electrical
Nov 9, 2018
35
hello, what does two-stack type switchgear means?

mv_switchgear_lhbl93.png
 
Replies continue below

Recommended for you

Two breakers, one above the other, in a single cubicle of gear.

I’ll see your silver lining and raise you two black clouds. - Protection Operations
 
Hello, davidbeach do you have brands which use the two-stack type?
Was it ANSI or IEC?
 
All ANSI, but every line of switchgear I’ve looked at includes stacks as well as singles. No idea about life in the IEC world.

I’ll see your silver lining and raise you two black clouds. - Protection Operations
 
Hi, It implies that breakers are arranged in 2 tier fashion, 2 breakers in a vertical section.
 
Dear Mr. PoliPoliCarps 8 Jul 21 02:35
" hello, what does two-stack type switchgear means?
do you have brands which use the two-stack type?
Was it ANSI or IEC?
"

1. If you look into any manufacturer LV switchgear catalogues, you will see what is "two-stack" as explained. For LV switchgear there are even "three-stack".
2. For MV due to bigger physical size up to say 22kV with vacuum or SF6 breakers, there are "two-stack" design available on the market.
3. This is applicable to IEC or ANSI world.
Che Kuan Yau (Singapore)

 
Low voltage is 4, medium voltage is 2. Low voltage is almost always 4, but for MV, industrial/commercial customers almost always go 2 but utility customers often limit it to one per section.

I’ll see your silver lining and raise you two black clouds. - Protection Operations
 
Status
Not open for further replies.