RobbieDicks
Electrical
We have been testing/inspecting 250 to 750 HP motors (mainly DC with separately excited fields) for several years at a customer of ours. Between my colleague and myself (both of us engineers) have developed a process to visually inspect the communtator, brush lengths, and motor insulation. We typically use a megger to test the insulation and have used the "twice the voltage" idea to safely perform the test. For example, if the output to the armature of the drive is 500VDC we output 1000V from the megger and record the results after a couple of minutes.
Likewise with the field, if the field voltage is 300VDC we output 500V from the megger.
Are these megger output values correct for testing DC motors?
I have yet to find a specific documented table of test voltages vs. motor voltages.
Likewise with the field, if the field voltage is 300VDC we output 500V from the megger.
Are these megger output values correct for testing DC motors?
I have yet to find a specific documented table of test voltages vs. motor voltages.