Megger Testing in Hazardous Location

Status
Not open for further replies.

powerjunx

Electrical
Sep 13, 2002
448
Hello,

Can anybody provide me any suggestions about standard practice or precautionary measures of conducting Megger Test in Hazardous Area containing Hydrocarbons. It is a topside electric motor pump as well as gauging instrument devices of loaded crude oil tanker. A link of brief literature is much appreciated.

Thanks.

"..the more, the merrier" Genghis Khan

 
Replies continue below

Recommended for you

WE cover these situations under our "Hot Work" permitting program, treating the megger test as a possible ignition source.

That means, in it's most basic form, examination of the worksite, including testing for flammable atmosphere.

old field guy
 
Hi, oldfield.. Can you provide me a link about your guidelines or checklist upon completing HOT Work Permit? Any adapted standard practice incorporated to your program? Thanks.

"..the more, the merrier" Genghis Khan

 
I also cover this work under a hot work permit. You would do a initial LEL check for gas, depending on your situation having a meter at the motor where you may be expecting a possible spark. Typically having someone man the detector that is in the hazardous area if your are testing from a remote location...MCC,motor disconnect,ECT....
 