Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Metal floor deck attachment to bar joists

Status
Not open for further replies.

dylansdad

Structural
Nov 15, 2005
134
I have searched thread titles and do not seem to find an answer to what I think is a simple question. I have specified a 1.5" composite metal deck for a floor assembly and the deck supplier came back with questions such as support pattern for 5/8" welds, spacing at perimeter supports and sidelap fasteners per span. I have chosen a 36/4 pattern for perpendicular to supports, but is there a typical spacing between supports (5/8" weld) and sidelap (#10 TEK) per span? Thanks.
 
Replies continue below

Recommended for you

Generally speaking that fastener spacing, both main support and sidelap, are a function of your diaphragm requirements.

If you take a look at the manufacturer's information they have the capacities listed for different fastener spacings.

For low load diaphragms, we specify the welds for a 36/4 pattern at supports and button-punched or screwed sidelaps at 24" o/c.
 