apprenteng
We do have a client metered on 11kV. The facility is fed via two 11kV lines, initially supplied via a single feeder,A. Feeder B was on stand by but could be connected to the bus via an airbreak switch when A had a permanent fault. A changeover using voltage as the actuator was used. Both lines are now energized upto the respective breakers on request by the client,and a manual change over is carried out to the other feeder when onegoes off. The facility has one meter and the utility is not ready to instal another meter. I am trying to come out with a new autochangeover for the VTs; I have parralled the currents from CTs on both feeders to the meter but I need to have an autochange-over for the VTs.
The tie breaker is ever on and using loss of voltage as a change over mode is not possible anymore since both lines are usually energized upto the respective breaker. I thought of using the breaker contacts but the utility may not allow this for the purpose of integrity,lest they steal power... The diagrams are attached. Any suggetions?!
Note: The incoming cable confuration was ahd to be modified as shown in the diagram for the purpose of phasing out with the clients loads.