Hi all,
It is proposed to have a storage mezzanine built into an existing single storey tilt panel building. It only partially covers the plan area of a unit and its attachment to the existing building is to 2 parallel tilt walls (at 3m elevation of 6m tall panels), which I'm happy to utilize for seismic forces in the walls in-plane direction. As proposed, only 1 line of walls/bracing is supplied perp. to existing walls, leaving an open-ended diaphragm - this leads to a demand on the new framed wall that can't be met without steel bracing and new footings cut into slab. The other alternative is to place the demand on the existing walls in out-of-plane bending between the ground floor slab and the roof bracing.
This is something I don't feel entirely comfortable with because
1) The existing walls are 150 thick, centrally reinforced with Low ductility mesh which does not meet minimum R/F requirements (all too common here in Australia - for some reason we chose to "cherry pick" ACI provisions)
2) Displacement incompatibility with roof diaphragm/bracing, which could create larger anchorage forces (indeed this may be an issue even if mezzanine can laterally support itself but is anchored to existing walls.)
3)Calculations suggest wall can cope with "elastic" design level forces (without any reduction factor), yet capacity of wall to cope with seismic forces beyond design level would be limited/brittle and mid-height hinging would in my opinion be detrimental to wall stability and the integrity of the mezzanine anchorage (failure of mezzanine gravity support).
4) Don't like the idea of "leaning" heavily loaded beams and columns on the out-of-plane stiifness/strength of panels.
Was hoping for others opinions, experiences with this structural configuration and if my worries utilizing the out-of-plane capacity of the walls are unfounded?
Thanks
Toby
It is proposed to have a storage mezzanine built into an existing single storey tilt panel building. It only partially covers the plan area of a unit and its attachment to the existing building is to 2 parallel tilt walls (at 3m elevation of 6m tall panels), which I'm happy to utilize for seismic forces in the walls in-plane direction. As proposed, only 1 line of walls/bracing is supplied perp. to existing walls, leaving an open-ended diaphragm - this leads to a demand on the new framed wall that can't be met without steel bracing and new footings cut into slab. The other alternative is to place the demand on the existing walls in out-of-plane bending between the ground floor slab and the roof bracing.
This is something I don't feel entirely comfortable with because
1) The existing walls are 150 thick, centrally reinforced with Low ductility mesh which does not meet minimum R/F requirements (all too common here in Australia - for some reason we chose to "cherry pick" ACI provisions)
2) Displacement incompatibility with roof diaphragm/bracing, which could create larger anchorage forces (indeed this may be an issue even if mezzanine can laterally support itself but is anchored to existing walls.)
3)Calculations suggest wall can cope with "elastic" design level forces (without any reduction factor), yet capacity of wall to cope with seismic forces beyond design level would be limited/brittle and mid-height hinging would in my opinion be detrimental to wall stability and the integrity of the mezzanine anchorage (failure of mezzanine gravity support).
4) Don't like the idea of "leaning" heavily loaded beams and columns on the out-of-plane stiifness/strength of panels.
Was hoping for others opinions, experiences with this structural configuration and if my worries utilizing the out-of-plane capacity of the walls are unfounded?
Thanks
Toby