stegall
Electrical
- May 18, 2006
- 1
Hi,
We have a new system with a bus bar protection scheme comprising of an Areva MFAC Relay (BBP), MVTP Relay (CTS), Metrosil & Variable Resistors all in parallel with each other.
The CTS has operated on a couple of occasions, and measurements were taken that highlighted ~20mA of 'spill' current.
The settings on the BBP are set fairly low (as per the spec) - would it be feasible to increase the value of the shunt resistor to de-sensitise the CTS?
My senior doesn't want to arrange a needless shut down and I am a recent graduate with not a lot of experience in the field.
Other thoughts are faulty CT somewhere on the scheme, or mismatched CTs?
Kind Regards