I'm checking a building foundation on micropiles. Soil is a mixture of sand and gravel, weight about 19kN/mc, phi= about 40°; design lenght is about 11m and water table is about 7m under pile cap.
The designer computed an allowable load of about 43tons according to Bustamante & Doix, but I think it is reallly too high for a micropile of 11m, even in gravel.
Depending on different theories I get 15tons to 20 tons allowable load.
Anyway it is the 1st time I heard about Bustamante & Doix. Does anyone know something about it ? Is 43 tons consistent with micropiles ?
Thanks
Ale