Dear engineers,
For one of my projects, the vendor has selected a computer room air-conditioning unit (CRAC). The selection parameters are as below:
Supply air temperature from the unit = 19 deg C
Return air temperature to the unit = 30 deg C
Net sensible cooling capacity = 110 kW
But, as per the revised design requirements, the return air temperature shall be 23 deg C. With the same CRAC unit selected above (110 kW) and with the revised return air temperature of 23 deg C, the vendor mentioned that the unit can supply the air only to as low as 17.5 deg C but not below it (and hence it can deliver only 56 kW cooling capacity).
Can anyone clarify, which parameter of the coil limits the lowest supply air temperature from the unit? Why can't the same unit supply the air at 11 deg C, so that the sensible capacity is 108 kW or supply at 9 deg C, such that the sensible capacity is 126 kW? (The chilled water supply and return temperatures are 10 and 17 deg C).
This question may seem basic/preliminary, but hope to get a clarification from any of the experts.
Thanks.
Thanks.