Here is the UL text on bar joists:
[blue]7. Steel Joists
The specified minimum-size joist in floor- or roof-ceiling designs is the joist that meets the requirements for both the minimum depth and the minimum weight per foot. Joists that exceed the specified minimum size may be used, provided the accessories are compatible. The dimension from the bottom chord of joists to the ceiling, whether given or calculated, is a minimum.
Spacing between joists may be increased from that specified to a maximum of 4 ft on centers if the floor slab meets structural requirements and the spacing of the hanger wires supporting the ceiling is not increased. Where it is necessary to provide support for the ceiling hanger wires between the joists, this may be accomplished by using 1-1/2 in., 16 gauge or larger cold-rolled steel channels. Each channel with its web oriented vertically should be placed on top of and perpendicular to the joist's bottom chord and tied thereto with a double strand of 18 SWG galvanized steel wire.
The area of bridging bars or angles specified in the individual designs is a minimum. Larger bridging may be necessary in order to meet the structural and/or code requirements.....K-Series joists may be substituted for other joists specified in floor- or roof-ceiling designs as follows:[/blue]
And for beams...
[blue]1. Beam Size
For fire-resistance purposes, the minimum beam size is expressed in terms of a W/D ratio, where W is the weight of the beam per lineal foot and D is the perimeter of protection material at the interface between the steel section and the protection material. Accordingly, beams of the same configuration and having a greater W/D ratio than the beam size specified in the fire-resistive design are considered larger than the specified minimum-size beam and may be used in that design.
W/D values are published by the American Institute of Steel Construction. In 2001, the method used to calculate the perimeter was refined to include the fillets of hot-rolled sections rather than assuming right-angle intersections. An example of this change results in the W/D value for a W8x28 section changing from 0.80 to 0.819.
Application of equations in the Fire-resistance Directory that include proportional relationship of the (W/D) value are not affected by the change in the calculation process for (W/D), provided the (W/D) values used are determined by a single method....[/blue]
Here is the link to the info above:
Link to UL text