Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Minimum bearing for hollow core precast plank

Status
Not open for further replies.

andyfabian

Structural
Jul 2, 2003
33
US
Simple questions:

What is the minimum bearing requirement for hollow core precast plank?

What is the minimum steel beam flange width for interior bearing of plank from both sides of beam?

Thanks.
 
Replies continue below

Recommended for you

I don't know if there's an industry standard, but I usually use a minimum of 2-1/2" bearing, preferably 3" and usually use 1-1/2" or 2-1/2" untempered masonite or korolath bearing strips...

Dik
 
Many things to consider. I have a design and engineering handbook from Spancrete, which shows "minimum" (not necessarily acceptable) bearing requirements.

This manual shows 3.5" on masonry, 3" on embedded steel angle, 2.5" on steel beam, with 1" gap between abutted ends, you would need a 6" wide flange.

Thicker plank, with thicker concrete toppings, with longer spans, with higher live loads may require greater bearing. Check with the precast manufacturer and supplier for that job for final design requirements.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top