sdz
Structural
- Dec 19, 2001
- 555
9.1.4 Minimum design actions on connections
Connections carrying design action effects, except for lacing connections and connections to sag rods, purlins and girts, shall be designed to transmit the greater of—
(a) the design action in the member; and
(b) the minimum design action effects expressed either as the value or the factor times the member design capacity required by the strength limit state, specified as follows:
I've read the commentary and I'm still confused.
e.g. the commentary says "For columns that may be subject to large compressive forces and only minor tensile forces, any splice has to be designed both for the specified value for the minimum member size required to resist the compression, and for the specified value for the minimum member size required to resist the tension."
Since you can base the minimum design action on multiple minimum theoretical member size when would these rules ever apply?
For a brace member (which is what I'm looking at now) if you are required to design for 0.3 x capacity of minimum tension and compression members individually then since those minimum (theoretical) members will be working at 100% of the design load the "Minimum design actions on connections" will always be less than the calculated loads.
Have I missed something here?
Connections carrying design action effects, except for lacing connections and connections to sag rods, purlins and girts, shall be designed to transmit the greater of—
(a) the design action in the member; and
(b) the minimum design action effects expressed either as the value or the factor times the member design capacity required by the strength limit state, specified as follows:
I've read the commentary and I'm still confused.
e.g. the commentary says "For columns that may be subject to large compressive forces and only minor tensile forces, any splice has to be designed both for the specified value for the minimum member size required to resist the compression, and for the specified value for the minimum member size required to resist the tension."
Since you can base the minimum design action on multiple minimum theoretical member size when would these rules ever apply?
For a brace member (which is what I'm looking at now) if you are required to design for 0.3 x capacity of minimum tension and compression members individually then since those minimum (theoretical) members will be working at 100% of the design load the "Minimum design actions on connections" will always be less than the calculated loads.
Have I missed something here?