Minimum ground clearance required as per IEC for Transmission line

Status
Not open for further replies.

balaji.srinath

Electrical
Dec 8, 2016
3
0
0
IN
Hi all,

In which IEC, it is mentioned the minimum ground clearance for different voltage transmission lines.

Regards,
Balaji
 
Replies continue below

Recommended for you

Google say 60071

Did you even try to do some research?

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
@ balaji.srinath
Did you try IEC 61936-1 title Power installations exceeding 1kV AC and 1.5kV DC Pt 1.. See whether any data therein that your are looking for.
Che Kuan Yau (Singapore)
 
Hi littleinch & che12345

In both the IEC standards 60071 & 61936, Ground clearance w.r.t Transmission line is not mentioned..only phase-phase & phase-earth (conductor - conductor & rod - structure) is mentioned w.r.t BILs.

Regards,
Balaji K
 
Clearance above ground seems to be a country by country thing based on historical clearance and country specific reasons.

Most trucks are max 5m, maybe 5.5 so add that to the phase to earth distance and add a bit for safety.

The "bit" probably varies between countries.



Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
Hi Balaji,
to my knowledge, the only requirements regarding clearances are reported in the European Standard EN 50341-1. 
In principle, the armonized standard requires basic clearances and reports the attendant formulae.
A "basic" height of 5 m is assumed for objects beneath OHLs in "normal" areas; electric (lightning or switching) clearances shall be added to the 5 m to obtain the clearances.
National annexes (EN 50341-2-XX) report specific values for each country.


Si duri puer ingeni videtur,
preconem facias vel architectum.
 