Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

minimum reinforcement for concrete duct bank

Status
Not open for further replies.

h-badawy

Structural
Jan 8, 2015
132
Dear experts

shall we follow ACI-318 code for minimum reinforcement of slab for concrete duct banks or is there any topics i can follow for this issue?

Thank you
 
Replies continue below

Recommended for you

What level of crack control do you need?
 
Typically, duct banks are not considered structural concrete and as such are not bound by the minimum reinforcement requirements in ACI. I have seen many with little or no reinforcement perform very well. If it were my design, I would provide the minimum reinforcement for crack control even if it was not required by code
 
I agree with the others. Chapter 7 of ACI 318 lists minimum area of shrinkage and temp reinforcement. The values vary between .14% and .2% depending on the grade of steel used. Also, don't forget your minimum clear cover and maximum reinforcement spacing.
 
Unless they're deeply buried or very large I would just put in temp. & shrinkage rebar in a single layer, middle of the walls/slab. If they're getting driven over with little soil cover I might throw in some distribution rebar in the top and bottom slabs.

Professional and Structural Engineer (ME, NH, MA)
American Concrete Industries
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor