Minimum reinforcing in footing 1

Status
Not open for further replies.

m1208

Structural
Apr 6, 2011
69
For isolated concrete footing, I check the required flextural rebar with 0.002bh (minimum) and the temperature rebar with 0.0018bh. Is this a conservative method when the foundation depth is shallow?
 
Replies continue below

Recommended for you

In some environs, footings are exempt from minimum flexural reinforcing requirements. For small footings I often use unreinforced plain concrete. If your minimum steel meets your flexural needs, then you should be run with it.

Dik
 
For a long and entertaining thread on this topic - check out this:

thread507-251751
 