CURVEB
Structural
- Jul 29, 2013
- 133
I'm in a jurisdiction that uses IBC 2015 and requires a minimum seismic design category of B. I'm curious how other engineers are implementing minimum requirements.
I'm currently working on a project that would be SDC A based on the soil site class and acceleration parameters. Do you increase the Ss and S1 factors so that you have the minimum Sds/Sd1 to correspond with Design Category B? Or do you keep Ss and S1 and increase Fa/Fv? Either of these options would increase your Cs factor, but I'm not sure which ones are appropriate to change. S1 is used to calculate the lower-bound limit on Cs in some cases, so it seems like that variable would need to be adjusted as well.
The other option would be to keep all of the parameters the same, use Cs for the SDC A calculation, then simply make sure you are meeting all of the detailing requirements for SDC B.
I'm currently working on a project that would be SDC A based on the soil site class and acceleration parameters. Do you increase the Ss and S1 factors so that you have the minimum Sds/Sd1 to correspond with Design Category B? Or do you keep Ss and S1 and increase Fa/Fv? Either of these options would increase your Cs factor, but I'm not sure which ones are appropriate to change. S1 is used to calculate the lower-bound limit on Cs in some cases, so it seems like that variable would need to be adjusted as well.
The other option would be to keep all of the parameters the same, use Cs for the SDC A calculation, then simply make sure you are meeting all of the detailing requirements for SDC B.