MTLoeb
Structural
- Aug 4, 2019
- 14
I wonder if anyone has a clear reference for the tie bar requirements in a trench footing. For this example lets say we have a 2'-0" deep footing thats 1'-8" wide. Cast against dirt so 3" cover, and (3) #4 bars top and bottom with ties at 16" o.c....Oh No! the clear spacing of our longitudenal bars is 6.3 inches. Thats greater than the 6" allowed per ACI 318-14 chapter 25. Now I lean a direction wich im trying not to put out here, but the tie bar requirements need additional support past 6" clear cover.... but we are only providing this much rebar because of minimums required by the area of concrete. It's not like we need this trench footing to be this wide the whole depth, this is just commom construction practice in some area. you could say, why reinforce concrete that is not structurally needed, or maybe that chapter 25 references a research paper about columns for that section, so it doesnt apply to us....well, what do you do typically if you have this situation, is another vertical #3 tie needed?
Thanks
Thanks