Thanks for the answer.
Normally I use shunt tuned filters that I design, like the image, and installed at the output of a transformer or generator. I've rarely used active filters.
I was thinking and looking for another solution, to use together with VDF and DRIVES passively, so I found Mirus and MTE.
About your image and calculations:
- the voltages and currents of Xin and Xout are at 50Hz?
- the voltage and current of Xcap at 250Hz?
- What is the nominal voltage of the system?
I used your data in a simulation, and found resonance peak around 130Hz, maybe my data is wrong.
When the load is too low, can the voltage increase from + 10% at point A3 according to its design? do you have some measurement about it?
I used in the simulation:
Xin = 0.299 ohms for 50Hz
Xout near Xin
Xcap = 0.0976 ohms for 50Hz
C = 2.44 ohms for 50Hz
shunt tuned harmonic filter
circuit
ressonance paek