Mitigation of Transferred Potential

Status
Not open for further replies.

Kiribanda

Electrical
May 6, 2003
697
Hello members,
It is an industry practice to separate two ground rods by 2 times the rod length
so that one is not influenced by the other. Similarly, to mitigate the transfer of GPR
as a transferred potential from SUB A to SUB B, instead of sharing a single ground grid for
both subs, is it acceptable to install two individual ground grids for SUB A & B separated by
minimum of 100m so that one grid is not influenced by the other?
Is there any any code or standard recommendation

 
Replies continue below

Recommended for you

Similar to the ground rods comparison, the separate between Grid A and Grid B will be based on their maximum dimension (as well as the soil structure), as that drives the zone/sphere of influence of the soil potential.

I'm not aware of a guide/standard that is direct to your question, however we can consider the measurement process for the Fall of potential in IEEE Std 81. Essentially your grids can be 3-6x the maximum grid dimension(s) away from so that they do not conductively couple.

With substation grounding systems there may be shield wires or neutrals that metallically connect grid A and B so this isolation may not be possible.
 
In Power plants it is a requirement to interconnect the plant earth grid and the Switchyard earth grid. These grids may be separated by a distance of about 100m.
 
This question has arisen locally in the context of separated HV/LV earth systems in utility system. The standard answers I am aware of consider the relative size of both grids.

Since you wish to segregate based on the transferred potential via the earth itself, to achieve what you want, you must consider all connections to earth and possible parallel paths. The recommendation by @DBL-E is good, however you need to be considering using software modelling if you need a truly reliable answer.
 