Mitsubishi FX1N DI reacting on negative state

Status
Not open for further replies.

VLADOAP

Electrical
Sep 12, 2019
1
Hello,

I have some troubles with FX1N plc.
The problem is that digital inputs react only when there is negative state ( 0V and not when there is +24V). I’m using Gx developer software with ladder logic. What may cause that problem? I’m new in PLC programing.
Thank you!
 
Replies continue below

Recommended for you

You need to lookup and understand "source and sink logic". That will flip the state of an input, or output, for that matter. Also, a lot of newer PLCs will allow both with a single model of I/O card. It's up to the user which way they wire it as to whether a 0V or 24V input is seen as an active input.



Keith Cress
kcress -
 
Assuming your input module is for a sinking type input, you may need to use a pull-up or pull-down resistor to set the input voltage when the input device is off. Something link a 5Kohm resistor tied to the appropriate (high or low) voltage will usually work.