Mixing Types Cables in conduit or tray.

Status
Not open for further replies.

ksavoie

Electrical
Mar 6, 2006
24
Is it OK to mix 300v Cable and 600v Cable in the same condit or tray if all cables will be used at a voltage of 24v?
 
Replies continue below

Recommended for you

NFPA 70-2005
392.6 (E) Multiconductor Cables Rated 600 Volts or Less.
"Multiconductor cables rated 600 volts or less shall be permitted to be installed in the same cable tray."

I think you're covered.
 
JMatt,

Thanks for the info. on the multiconductor cable and Tray. Does anyone else know where I can find the same infomation for conduit? I was told I can't mix 300v and 600v cables in the same conduit even though the voltage is 24v for all cables.

 
It's the same for conduit, enclosures, or any raceway. NEC Article 300.3(C)(1).

Over 600 V it's a different story.
 