rockman7892
Electrical
- Apr 7, 2008
- 1,161
Does anyone have experience with modeling a PV inverter in order to model short circuit fault contribution into an existing distribution system?
From what I have looked at I see that the rule of thumb for an inverter's fault contribution is 1.5 - 2 times its continuous rating. Has anyone used these numbers or similar numbers?
What is the best model representation for the inverter interfacing with a distribution system? I'm using SKM and the first thing that comes to mind is using a utility source to model the inverters contribution although I'm not sure if this is the best option. Is there some better option for modeling the inverter fault contribution.
Also I don not have the system I am interfacing with modeled so I am going to provide a fault magnitude and X/R ratio at the POCC to the rest of the system. Can I use the cable and transformer impedances between the inverter and the POCC as the impedance component of the fault calculation at the POCC bus or is the fact that the inverter fault contribution may be dynamic change things somewhat?
Any thoughts on how this effects coordination in the distribution system as well? I am dealing with a 250kW inverter connecting to the distribution system at 480V through a 400A thermal-mag breaker. Is there any coordination considerations between this breaker and the POCC pane's main breaker? I know that an inverter is cable of disconnecting itself very quickly during a fault in some cases 1-2ms which then may not require coordination?
From what I have looked at I see that the rule of thumb for an inverter's fault contribution is 1.5 - 2 times its continuous rating. Has anyone used these numbers or similar numbers?
What is the best model representation for the inverter interfacing with a distribution system? I'm using SKM and the first thing that comes to mind is using a utility source to model the inverters contribution although I'm not sure if this is the best option. Is there some better option for modeling the inverter fault contribution.
Also I don not have the system I am interfacing with modeled so I am going to provide a fault magnitude and X/R ratio at the POCC to the rest of the system. Can I use the cable and transformer impedances between the inverter and the POCC as the impedance component of the fault calculation at the POCC bus or is the fact that the inverter fault contribution may be dynamic change things somewhat?
Any thoughts on how this effects coordination in the distribution system as well? I am dealing with a 250kW inverter connecting to the distribution system at 480V through a 400A thermal-mag breaker. Is there any coordination considerations between this breaker and the POCC pane's main breaker? I know that an inverter is cable of disconnecting itself very quickly during a fault in some cases 1-2ms which then may not require coordination?