Question on desing/classification of a heat exchanger:

For commercial ice machine unit evaporators, with an ice cube forming mold. (for something like a Manitowoc or scottsman like unit) How would one model/design such a system(going back to fundamentals). Cross-flow or counter flow. In addition, how might one model account for the build up of ice?

thanks!
 
Replies continue below

Recommended for you

Hmmm... there seem to be a lot of info missing. I'd lot at your application... you say you are making ice cubes, so you might want a mechanical system that can sense when the cubes are frozen and remove them from a tray.
The heat exchanger might be an additional step that takes away some of your efficiency... unless I'm not understanding what you are doing or how.

 
Most evaporators are not considered parallel flow or counter flow since there is a phase change. You can model this evaporator as constant temperature on the refrigerant side (even though it is probably a DX unit with some superheat). On the water side it would be convection while the water is a liquid and then conduction when the water has turned to ice. Depending on your geometry (cube, tube, or other shape) you can easily model your heat transfer.
 
GEPMAN

THIS IS A GOOD APPROACH, MAKES TOTAL SENSE INTUITIVELY! THANKS
 