I'm trying find the correct way to model SWER. I'm aware some software's let you select the system type as SWER, but I'm stuck with just a 3-phase modelling software (PSS-ADEPT).
Can you represent SWER with sequence components in a 3-phase system? I've read that you can apply the Carson Equation to 1, 2, and 3 phase conductor systems, where I assume a 1 phase conductor system is identical to a SWER system?
So far I can produce the primitive impedance matrix as a 2x2 matrix: [[z_aa, z_ag],[z_ga, z_gg]], where z_aa is the self impedance of the conductor, z_ga = z_ag is the mutual impedance of the ground-conductor pair, and z_gg is the self impedance of the ground.
I have expressions for getting values for a z_aa, z_ag, z_gg from the physical parameters of the system. I can then use Kron Reduction to get rid of the neutral (is this step right, as Kron reduction requires 0 A current in the neutral and this technically isn't true because the neutral is the earth return path?) and produce a 1x1 matrix (scalar) that is the adjusted z_aa value (z_aa(new) = z_aa(old) - 2*z_ag/z_gg).
I then build the phase frame matrix [z_abc] = [[z_aa(new), 0, 0], [0, 0, 0], [0, 0, 0]]. Then proceed to do the typical thing: [z_012] = [A]^-1.[z_abc].[A]. Since the phase frame matrix is symmetrical we should expect to see 0 elements for the off-diagonal terms in the impedance matrix. This doesn't yield a meaningful result though.... so can someone explain where I might be going wrong, or what the correct approach is with SWER (and 2-phase/v-phase systems) and finding the zero, positive and negative sequence impedance.
I'm trying find the correct way to model SWER. I'm aware some software's let you select the system type as SWER, but I'm stuck with just a 3-phase modelling software (PSS-ADEPT).
Can you represent SWER with sequence components in a 3-phase system? I've read that you can apply the Carson Equation to 1, 2, and 3 phase conductor systems, where I assume a 1 phase conductor system is identical to a SWER system?
So far I can produce the primitive impedance matrix as a 2x2 matrix: [[z_aa, z_ag],[z_ga, z_gg]], where z_aa is the self impedance of the conductor, z_ga = z_ag is the mutual impedance of the ground-conductor pair, and z_gg is the self impedance of the ground.
I have expressions for getting values for a z_aa, z_ag, z_gg from the physical parameters of the system. I can then use Kron Reduction to get rid of the neutral (is this step right, as Kron reduction requires 0 A current in the neutral and this technically isn't true because the neutral is the earth return path?) and produce a 1x1 matrix (scalar) that is the adjusted z_aa value (z_aa(new) = z_aa(old) - 2*z_ag/z_gg).
I then build the phase frame matrix [z_abc] = [[z_aa(new), 0, 0], [0, 0, 0], [0, 0, 0]]. Then proceed to do the typical thing: [z_012] = [A]^-1.[z_abc].[A]. Since the phase frame matrix is symmetrical we should expect to see 0 elements for the off-diagonal terms in the impedance matrix. This doesn't yield a meaningful result though.... so can someone explain where I might be going wrong, or what the correct approach is with SWER (and 2-phase/v-phase systems) and finding the zero, positive and negative sequence impedance.