knfeng
Structural
- Dec 9, 2005
- 7
Need some help/advice with the following situation proposed an architect. A new elevator shaft and stairs are intended to be installed within an existing 3-story, 25 year old building. Framing system is 18" 'H' series bar joists @ 24" o.c. supported on exterior 4" brick/4" block (I'm assuming composite) w/ 4-1/2" concrete on decking.
The plan at the elevator is to build the shaft up thru the vertical space while the joists are left in place (removing the concrete and decking within the shaft space) and then provide some sort of connection/stiffening of the joist at the masonry walls. After the joist is supported the joist within the space can be removed.
The stair would be supported on new steel beams which would also support the existing bar joists, also cut back.
Has anybody done anything similar to this before. I do plan on contacting some joist manufactures and possibly SJI but wanted to get some other opinions, too.
Thanks in advance.
The plan at the elevator is to build the shaft up thru the vertical space while the joists are left in place (removing the concrete and decking within the shaft space) and then provide some sort of connection/stiffening of the joist at the masonry walls. After the joist is supported the joist within the space can be removed.
The stair would be supported on new steel beams which would also support the existing bar joists, also cut back.
Has anybody done anything similar to this before. I do plan on contacting some joist manufactures and possibly SJI but wanted to get some other opinions, too.
Thanks in advance.