BronYrAur
Mechanical
- Nov 2, 2005
- 798
I have run into a situation that I haven't seen before. I have been asked to make recommendations on a boiler system. The system has 10 Raypack boilers at 2,000 MBH each. The piping is weird. It looks like it may have been intended to be some form of quasi-primary/secondary with a 3-way valve in what would have been the bridge. The valve is not operating and is always in the position where the bridge (bypass) leg is closed. So this puts the main pumps in series with the individual boiler pumps.
They have been running this system for years. Flow from the main pumps is pushed through all boiler all the time. The non-operating boiler pumps are "free-wheeling" as the system pumps push through them. The water in those non-operating boiler is of course not heated and blends in with the heat water. There is a temperature sensor on the line leaving the boiler room that is used to attempt to maintain a setpoint.
These are non-condensing boilers that run year round. They provide not only building heat but also domestic water heating. I think someone had the bright idea to drop the setpoint as low as possible in the summer, which brought back water that was too cold. Their heat exchangers have been rotting away.
The suspected load is only about 10,000 MBH, so they only need about half of the boilers. Some are beyond repair, and I think right now they only have 6 boilers in service. The others are valved off. So they are pumping through 6 boiler all the time and running boilers as needed to make setpoint. The main system pumps have VFDs but they are in a fixed position. They have suggested removing the boiler pumps and replacing them with 2-position valves. That way, there would be no pumping through non-operating boilers. I have concerns about this because the system flow would then be limited to the the number of operating boilers. Right now, nothing looks at the loads on the other end. I can foresee the loads not getting enough flow, which will not only be unsatisfactory, it may also lead to too low return water temp. The load consists of 4 heat exchangers, 3 of which have 3-way valves. So this will lead to highly variable flow (depending on the number of boilers), which doesn't seem like it will work. Also, the min/max range on the boilers is not very large. I am struggling with whether or not this "primary-only" type of system would be a good idea.
My first thought was to remove the 3-way valve and create a true primary/secondary bridge. That way, the boiler pumps and the system pumps would have hydraulic separation. I don't think the boiler pumps have enough head, but that can be fixed. The temperature sensor would also need to be moved so that it is on the other side of the bridge.
A sketch is attached. Any thoughts?
They have been running this system for years. Flow from the main pumps is pushed through all boiler all the time. The non-operating boiler pumps are "free-wheeling" as the system pumps push through them. The water in those non-operating boiler is of course not heated and blends in with the heat water. There is a temperature sensor on the line leaving the boiler room that is used to attempt to maintain a setpoint.
These are non-condensing boilers that run year round. They provide not only building heat but also domestic water heating. I think someone had the bright idea to drop the setpoint as low as possible in the summer, which brought back water that was too cold. Their heat exchangers have been rotting away.
The suspected load is only about 10,000 MBH, so they only need about half of the boilers. Some are beyond repair, and I think right now they only have 6 boilers in service. The others are valved off. So they are pumping through 6 boiler all the time and running boilers as needed to make setpoint. The main system pumps have VFDs but they are in a fixed position. They have suggested removing the boiler pumps and replacing them with 2-position valves. That way, there would be no pumping through non-operating boilers. I have concerns about this because the system flow would then be limited to the the number of operating boilers. Right now, nothing looks at the loads on the other end. I can foresee the loads not getting enough flow, which will not only be unsatisfactory, it may also lead to too low return water temp. The load consists of 4 heat exchangers, 3 of which have 3-way valves. So this will lead to highly variable flow (depending on the number of boilers), which doesn't seem like it will work. Also, the min/max range on the boilers is not very large. I am struggling with whether or not this "primary-only" type of system would be a good idea.
My first thought was to remove the 3-way valve and create a true primary/secondary bridge. That way, the boiler pumps and the system pumps would have hydraulic separation. I don't think the boiler pumps have enough head, but that can be fixed. The temperature sensor would also need to be moved so that it is on the other side of the bridge.
A sketch is attached. Any thoughts?