MechEngNCPE
Mechanical
- Feb 8, 2011
- 236
Ok, so I just wanted to post this to get a feel of what the community thinks on economizer relief/exhaust damper modulation when the ahu has both supply and return fans on vfd's, the supply vfd modulating off supply duct static pressure, and the return vfd modulating off space static. During normal operation the OA damper modulates off DCV control from a CO2 sensor in the return duct. During economizer operation the OA damper and RA damper modulate to provide 55 LAT. I have the exhaust air damper set to modulate to provide a -0.2" supply fan inlet pressure. We have airflow monitoring stations on OA, RA, and SA for the BMS to view and also set an OA airflow if they want. Does anyone see anything wrong with this setup, besides it being a controls nightmare? Oh, and this is VAV setup with about 40 DDC VAV's.