I’ve been away a few days and haven’t been able to respond…
The fan cfm tracking is your minimum outdoor air. If total building exhaust is 1700 cfm, you might set your return fan to track supply by 2,000 cfm, to make up for that exhaust volume and pressurize the building.
If you track the supply and return fans the right way, the position of the outdoor air dampers is negligible, as long as they are open sufficiently.
You keep this fan flow tracking and modulate the relief and return dampers to maintain your desired conditions, NOT your outdoor air damper.
You said “Why waste energy on using chilled / hot water?” You may have misinterpreted what I said; Read back. I’ll leave this as is…
I think you might be too quick to interpret what I’ve said so as to classify it as a “standard solution.” I am offering you the best solution. You don’t have to take it.
317069, for your questions. Responses to each are below:
"When minimum outdoor air conditions are required (maximum heating during winter or maximum cooling during summer), the economizer dampers modulate to minimum outdoor air. This is: outdoor air ~50% open, return 100% open, and relief/exhaust 100% closed" do you mean 5% or 50%?
I mean 50. It could be 100% or maybe 75% if you’d like.
- "Do NOT do CO2 control. It's a fallacy. It can be used to increase ventilation as needed but should not be used as sold, as a ventilation reduction" if we use it to increase ventilation why don't we do for reduction?
If you design a car, its idle speed should be 55 miles per hour, right? 55 mph might be needed at some point. But if you’re in residential neighborhoods or back roads, you should put on the brakes every now and then because the 55 mph might not be needed… Or should you have the car idle at 5 mph and increase toward the 55 value if conditions demand?
- "If this does not resolve the AHU DAT conditions, the chilled or hot water valve should be used (without overlap) to maintain the design conditions." Could you please expalin what do you mean by overlap, for example let say we have a space needs to be at 75dbF and 50%RH, the out side air is 65F, its enthalpy is less than space enthalpy, economizer is enabled( enabeled doesn't mean started)could you please tell what are the positions of OA, RA, EXA dampers and chilled water valve would be?”
Yes. If the AHU DAT set point is 55 while the condition you describe is in progress, first modulate the relief and mixing dampers toward full outdoor air. Because it’s 65 out and you can’t get enough free cooling, then slowly modulate the mechanical cooling. Ensure via programming that heating and cooling can’t happen at once. In pneumatics (old school) operation of the two were separated by a few psig control air pressure. It was mechanically assured that the two would not operate at once.