Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Moment calculation of semi-circular or triangular two-way slabs 6

Status
Not open for further replies.

Pretty Girl7

Civil/Environmental
Nov 30, 2022
78
I noticed that the BS8110 AND Eurocode2, suggested some tables of coefficients (Table 3.14) to calculate moments occur in two-way slabs. But they are rectangular, and further I noticed they can't be used if the slab length is more than twice the width.

What if I have a triangular or semi-circular slab? which are also somewhat common in buildings.

Screenshot_2023-04-16_at_9.08.59_pm_ybp5qa.png


what are the methods to calculate moments in triangular, semi-circular and rectangular slabs? (not talking about design software)
 
Replies continue below

Recommended for you



Just sharing my experience ;

- draw the biggest dia. circle in the slab , then calculate the slab assuming one way slab with span dia of largest circle ,

- develop a FEM and see the effects if you need more refined calculation..






I cannot give you the formula for success, but I can give you the formula for failure..It is: Try to please everybody.

 
I would use a simple approximation, eg a one way strip through a representative area.
 
There exist no closed-form elastic solutions for arbitrary slabs. Your best bet is the yield line method or FE software.
 
Thank you all for your information and insights.
 