Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Moment of Inertia and Cross-Sectional Area

Status
Not open for further replies.

SPR Baker

Structural
Nov 12, 2017
50
Dear all
I don't understand these points:
Table 6.6.3.1.1(a)-[---] at Factored Load Level
Table 6.6.3.1.1(b)-[---] at Factored Load
What means of these words "Factored Load Level" and "Factored Load" ?
Please see attachement.
Thank you.
T1_svgpl3.png
 
Replies continue below

Recommended for you

Factored load level refers to an ultimate limit state (ULS) (i.e. safety critical, if it exceeds this it may fail). Unfactored loads, also sometimes called service loads, refer to a serviceability limit state (SLS), which is not safety critical (i.e. how do people feel using this building day-to-day; does it deflect too much? vibrate too much?).

The factors shown in your image refer to the stiffness modifiers when analyzing at the ULS. At the ULS, concrete will typically be cracking or entering the plastic deformation region, resulting in lower stiffness and larger deflections, possibly driving a P-Delta effect and increasing loading. Because we typically complete elastic analyses (which are linear), we need to account for that lower stiffness that results from the plastic region & cracking (which are non-linear effects). These stiffness factors account for that lower stiffness, allowing P-Delta and other increases to be accounted for at ULS using elastic analysis.
 
Thank u for nice explaination but
I am stil uncertent to use these tables and when use table 1 and when use table 2? And i don’t understand the word “Factored Load Level” and Factored Load? What really mean?

Table 6.6.3.1.1(a)-[---] at Factored Load Level
Table 6.6.3.1.1(b)-[---] at Factored Load
 
You may use either table, but just be consistent. Table 6.6.3.1.1(a) is for use where you don't want/need to be extremely accurate with your stiffness reduction or don't know your load levels yet, and you apply the factors to everything equally. This essentially assumes all elements are losing stiffness equally, which is likely incorrect but close enough to capture the (already imprecise) non-linear effects. It is quicker and easier, but doesn't account for load levels in specific members. Table 6.6.3.1.1(b) is for where you wish to be precise and where you know your loads. It can be applied at ultimate or at service levels (by changing to applicable P and M). It requires iteration and is more time intensive, but may yield slightly better results. It remains capped between the moment of inertia calculated by Table 6.6.3.1.1(a) and a value with a stiffness reduction factor (phi_K). It's up to you to determine whether the additional time is worth the additional accuracy, although I doubt it will be worth it in typical cases.

If you're hung up on "factored load level" vs "factored load", I'm pretty sure they should both read "factored load level".
 
What Level load refers?
It means we apply the stiffness reductions when the floor/Level experiences the tension stress exceed the limit Tension Stress ?
I want to clear this point or can you share doc relate to these questions?
Thank you
 
The factored load level refers to a degree of loading that includes an increase factor to account for the possible variation in the actual loading conditions.
 
Just to be clear, you need to apply the moment of inertia reduction for any ultimate limit state analysis where the moment exceeds the cracking moment. For most well proportioned structures this is always going to be the case. It has nothing to do with floors/levels experiencing tensions that might exceed the tension stress limit..
 
Factored Load Level and Factored Load are the same. Poor editing of the table titles.


A Great Place For Engineers to Help Engineers

Follow me there.....
 
Replace "at factored load" with "under ultimate limit state loading".

Replace "at factored load level" with "under ultimate limit state loading". As others have said, the word 'level' doesn't change the meaning at all.

It has nothing to do with ground floor, first floor, or second floor of a building. It only relates to the loading (ultimate limit state).

It's your choice whether to use table A or table B.
 
Thank u I got the point
And how about service check (Drift Check) should I need also reduced? And how much for stiffness reduction?
Thank you
 
Hi Phearun Seng

As per the last paragraph on the screenshot you posted, the answer is right there:-
Capture_jnr9zm.png
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor