Moment of Inertia? 1
veritas
467
Hi
I have an 11kV, 50Hz, 4.818MVA, 16-pole hydro generator. Shaft height = 1m, width = 1.95m. Any idea what the moment of inertia in J in kg.m2 is please? or what is a typical value for this type of machine. Have tried the manufacturer but it's like trying to pull chicken teeth!
Thanks in advance.
in the vicinity of 5000-7000 kg-M^2, but the OEM should have this information.
In my opinion, if the rotor weight is known and rotor diameter also then
J=GD^2=1/8*W*D^2 W=weight in kg ; D=rotor diameter [m]; J [kg.m^2]
If it is not known ,we may use the H constant formula:
J=2*H*Srated/(2*π*Frated/N)^2[kg.m^2]
Where H constant [2-4 Ws/VA]; Srated [4818000 VA]; Frated =50 Hz N=number of pole pairs[8]
In your case it could be 12500 to 25000 kg.m^2.
The above formula it is the same as per IEEE Std 399/1997 Brown Book 4.9.3.3.2 The H constant.
See[for instance]:
file:///D:/D_My%20Documents/Engineering/Generators/Synchronous%20generator%20dynamics%20Lund%20Un.pdf
7anoter4
Still working through your equations. First one no problem. Busy with 2nd one.
I did finally manage to get the rotor data from the OEM. The stated J = 2723 kg·m2 is substantially lower than the predictions in this post and I'm wandering why?
However, if I use the equation for J = m·r2/2 (identical to your first equation) = 3080kg·m2 as follows:
Add up the weights of the fan + shaft + magnetic wheel + rectifiers + exciter = 14582kg
Assume radius, r = 0.65m (approximately) to get
J = 14582*0.652/2 = 3080kg·m2 which is in the ballpark of 2723kg.m2
 http://files.engineering.com/getfile.aspx?folder=30b964f3-46be-4c09-93c3-826be0a8e1c1&file=Rotor_Data.pdf
What I also find intriguing is the following:
H = K/Sr = (5.48e-6·J·N2)/Sr =(5.48e-6·2723·3752)/4818000 = 0.436 J/VA.
where K = kinetic energy at rated frequency in Joules
Sr = rated power in VA
N = speed in rpm
Also a bit outside the range of 2-4 Ws/VA.
7anoter4,
Your 2nd formula, J = 2*H*Sr/(2*Π*f/N)2 is the same as mine. I used rpm instead of frequency and pole pairs. If H = 0.436, I get J = 2723 again using your formula.
Still a bit perturbed by the substantial discrepancy between the OEM values for J and the values suggested in this post.
Have you left out the hydraulic end of the shaft? All of that rotating mass counts too.
It does not help here, I was about to say what you need is Fred, but we have already a post from a Fred, so you need a joe. He's the little old guy in maintenance who jealously guards all the original plant data. This is because he knows how difficult it is going to be to replace it - from manufacturers who merged or went out of business.
Joe retires and the new guy, usually with an MBA or what ever throws "all that old junk" out.
I have seen this time and time again!
I have seen the inertia checked from a free run down. It was done graphically, but was 40 years ago, so sorry cannot remember the details. It was done at low speed, to minimize windage. I don't know the practicalities of doing it in your case.
Ok, will check it out, thank you. The rather low J for the machine is in itself good and bad. Bad because the machine will "react" relatively more to system disturbances than a higher J machine which of course is not desired. Good in that it is easier detectable with something like ROCOF which I am setting up for Loss of Mains. Wonder where's the ugly...
7anoter4,
Sorry, could not open the attachment. Needs some Adobe Acrobat Extended Asian Language font pack which I unsuccessfully tried to install. Maybe an alternative way to resend?
An older Adobe Reader X (10.1.4) version opens the file correctly here on line.
When saving the file and attempting to read it, it does not open.
Capturing two screen shots and inserting them into a word document, I came up with this:
 http://files.engineering.com/getfile.aspx?folder=57cade7a-81b5-4b83-b7bb-a010769ce34a&file=Inertia_Moment_word_doc.docx
Many thanks dArsonval, got it.
7anoter4 - makes sense now.
Hoxton - I know what you mean. Thankfully, this is a new generator and the OEM is still around. Just not very good at communicating.
Regards.
I don't know if that was a typo, but there is no /2 involved here.
(2B)+(2B)' ?
A decade ago, I wrote an application note on calculating moments of inertia starting from the most basic concepts. Partly I was working through things myself to make sure I understood every step, but also I was seeing people make mistakes by plugging into formulas they didn't fully understand. Using weight values instead of mass and then forgetting to use "g" is a common mistake.
Anyway, I offer the app note here. Comments (even corrections!) welcome.
Curt Wilson
Omron Delta Tau
 http://files.engineering.com/getfile.aspx?folder=96ad1dc6-a47f-4332-91bc-5e96a02aaf1c&file=Calculating_and_Using_Moments_of_Inertia.pdf
electricpete,
J = m·r2/2 is the formula for the inertia of a solid cylinder of mass m and radius r rotating on its axis. Units are kg·m2 (SI). I have seen this in more than one reputable text on the subject. However, I will also be first to admit that I have taken it on face value as I have never delved into deriving it from first principles.
Reading through the excellent text of Curt, also verifies this formula.
So I am still interested to know why you say there is no /2?
My formula would apply for thin-walled hollow cylinder of radius R.
Yours would apply for solid cylinder of radius R.
I don't know which context you were working with.
(2B)+(2B)' ?
Yeah, the rotor of a generator is approximated by a solid cylinder, hence the formula I used.