MONEY COUNTING MACHINE HEAT LOAD

Status
Not open for further replies.

coldkeeper1

Mechanical
Apr 26, 2008
12
I´m doing a preliminary heat load estimate for a large bank´s money counting room. They are planning to use some kind of industrial-sized counters which even use vertical tank air compressors for some purpose. Any idea on where to obtain info regarding heat output or cooling requirements for such equipment? Thank you
 
Replies continue below

Recommended for you

The manufacturer, or his equipment's manuals?

TTFN

FAQ731-376
 
I would assume the electrical boys are hooking it up, worst case you use the breaker settings.
 
Thank you both for your answers.
There still no final selection of the counting equipment manufacturer. When you talk about breaker settings, is that used to calculate volt-amps and then get an approximate heat equivalent? Thank you.
 
No final selection does not mean that someone doesn't have some information. Whoever is making the selection should have datasheets for the equipment.

TTFN

FAQ731-376
 
Yes, the wattage consumed by the machines is the internal load for HVAC purposes. The breaker setting may easily be 2x the actual continuous load, but it's a place to start.
 