karimom
Structural
- May 21, 2019
- 20
I am working on a project where the geotechnical report specified that a monolithic slab is a required with thickened edge (see attached photo).
The line load will be on the exterior of the footing and will apply some eccentricity to it. I would assume from common sense that it would not overturn due to the shape of the footing (i.e. the whole slab is tied together). I just want to be able to back myself up with calculations on this one. I can't find a similar example in any text book.
The soils are good (3000 psf bearing capacity) and we're applying around 2kip/ft (factored). I think that with a 18" deep by 18" wide footing it should be good from rough bearing checks and experience but the traditional B/6 check for a strip footing doesnt seem to apply to this.
Can any one advise or point me in the direction of an example?
The line load will be on the exterior of the footing and will apply some eccentricity to it. I would assume from common sense that it would not overturn due to the shape of the footing (i.e. the whole slab is tied together). I just want to be able to back myself up with calculations on this one. I can't find a similar example in any text book.
The soils are good (3000 psf bearing capacity) and we're applying around 2kip/ft (factored). I think that with a 18" deep by 18" wide footing it should be good from rough bearing checks and experience but the traditional B/6 check for a strip footing doesnt seem to apply to this.
Can any one advise or point me in the direction of an example?