In the United States, in underground mining applications it is legally required that the source secondary transformer have a neutral point, and the neutral must be grounded through a resistor. The resistor value is chosen to limit the maximum phase to ground fault current to 15 amps or less. For a 3 phase 600 volt system, the resistor value will be 23 ohms or more. In all cases, the source transformer’s primary is delta connected. All loads on the transformer secondary are connected phase to phase. Ground fault detection relays are utilized for instantaneous tripping of the branch circuits if a phase to ground fault condition occurs.
After reading the preceding discussion, it appears that a primary wye connection whose neutral point is solidly grounded will permit secondary zero sequence current to flow. Furthermore, it appears that the magnitude of secondary zero sequence current will in essence only be impeded by the resistor.
Agree or disagree?
Thank You, Jim
In the United States, in underground mining applications it is legally required that the source secondary transformer have a neutral point, and the neutral must be grounded through a resistor. The resistor value is chosen to limit the maximum phase to ground fault current to 15 amps or less. For a 3 phase 600 volt system, the resistor value will be 23 ohms or more. In all cases, the source transformer’s primary is delta connected. All loads on the transformer secondary are connected phase to phase. Ground fault detection relays are utilized for instantaneous tripping of the branch circuits if a phase to ground fault condition occurs.
After reading the preceding discussion, it appears that a primary wye connection whose neutral point is solidly grounded will permit secondary zero sequence current to flow. Furthermore, it appears that the magnitude of secondary zero sequence current will in essence only be impeded by the resistor.
Agree or disagree?
Thank You, Jim