elmatador
Electrical
- Jun 10, 2009
- 22
Hello all,
We have a few medium voltage motors with a 50:5 core balance current transformer for each phase. Are there any issues with connecting the neutral of each CT together at the motor end so that you only run 4-wires back to the relay, where the fourth wire is the common neutral wire? Are there advantages to running 4-wire vs 6-wire? Wouldn't the 6-wire only add more overall length? Also does the location of the CT neutral ground affect the selection of the type of cable being used: i.e. 4 conductor or 6 conductor cable?
Also, I have read several threads about the grounding location and the general consensus appears to be grounding it at the building where the relay is located. I understand that the CT needs to be grounded at one location but is the location of the ground an important factor to consider with respect to voltage rise and shock hazard possibility?
We have a few medium voltage motors with a 50:5 core balance current transformer for each phase. Are there any issues with connecting the neutral of each CT together at the motor end so that you only run 4-wires back to the relay, where the fourth wire is the common neutral wire? Are there advantages to running 4-wire vs 6-wire? Wouldn't the 6-wire only add more overall length? Also does the location of the CT neutral ground affect the selection of the type of cable being used: i.e. 4 conductor or 6 conductor cable?
Also, I have read several threads about the grounding location and the general consensus appears to be grounding it at the building where the relay is located. I understand that the CT needs to be grounded at one location but is the location of the ground an important factor to consider with respect to voltage rise and shock hazard possibility?