To verify the dimensioning of the CTs of a motor differential relay are usually checked both the stability for external faults and the relay trip for internal faults or only the stability?
If the bus bar where the motor is has a very high short circuit level (i.e. 35 kA at 11 KV close to the generators without any intermediate transformer) I think that the trip of the differential relay should be more critical.
Indeed we should be sure that the relay could trip before the CT saturation. The stability in this case is less critical because only the motor starting current (obviously multiplied by a K factor taking care of the motor time constant) is passing through the CTs. In any case I would check both conditions.
Am I totally crazy or not? The point is that we get a quite great value for the CT VA.
Thanks in advance for any answer
If the bus bar where the motor is has a very high short circuit level (i.e. 35 kA at 11 KV close to the generators without any intermediate transformer) I think that the trip of the differential relay should be more critical.
Indeed we should be sure that the relay could trip before the CT saturation. The stability in this case is less critical because only the motor starting current (obviously multiplied by a K factor taking care of the motor time constant) is passing through the CTs. In any case I would check both conditions.