electricpete
Electrical
- May 4, 2001
- 16,774
We have a deep-well submersible pump driven by a 75hp 460v vertical induction motor, with nameplate FLA=87A.
The pump curve indicates maximum BHP is 63HP at 525gpm. BHP is lower if you increase or decrease flow from that point.
At 525 gpm AND 130psig discharge pressure we twice measured the currents. Both times we measured 90, 92, 94A. Voltage was 490v balanced within accuracy of our voltmeter.
We wondered how the pump could be overloaded above 75hp when pump is incapable of drawing more than 62hp. We did realize that the motor measured speed is 1775rpm while pump curve is based on 1760 rpm. Assuming a cubed-law variation of power we still conclude pump should not draw more than 64hp. [I have to remember to double-check the nameplate speed... I think it's around 1775rpm).
Based on the fact that the HP had to be going somewhere we suspected a rub. We had the maintenance dept adjust the pump lift. They did an adjustment and reported no signs of a rub (rotated smoothly). After the lift adjustment the current had decreased approx 2A to 88A, 89A, 92A (still 490V, still 130 psig/525gpm).
We varied flow by pumping to bypass. We confirmed that for any discharge pressure higher or lower than 130A, the current readings went down (this is in agreement with the shape of the BHP curve).
We cannot precisely determine the head of the pump since the suction pressure (far underground is unknown), but we believe the flow info is sufficient to locate us on the curve. We are perplexed that the motor can deliver more current than the pump appears capable of consuming on paper.
I don't think it is a problem with the motor itself since the motor has been replaced and the previous motor had similar high current draw. In fact this motor has been replaced about 3 times in last 10 years for various reasons I am not totally familiar with. It is a tough outdoor environment. With 1.15sf it should be able to withstand this level of overload but I would like to try to understand it better.
Any suggestions what might be going on or how to troubleshoot?
The pump curve indicates maximum BHP is 63HP at 525gpm. BHP is lower if you increase or decrease flow from that point.
At 525 gpm AND 130psig discharge pressure we twice measured the currents. Both times we measured 90, 92, 94A. Voltage was 490v balanced within accuracy of our voltmeter.
We wondered how the pump could be overloaded above 75hp when pump is incapable of drawing more than 62hp. We did realize that the motor measured speed is 1775rpm while pump curve is based on 1760 rpm. Assuming a cubed-law variation of power we still conclude pump should not draw more than 64hp. [I have to remember to double-check the nameplate speed... I think it's around 1775rpm).
Based on the fact that the HP had to be going somewhere we suspected a rub. We had the maintenance dept adjust the pump lift. They did an adjustment and reported no signs of a rub (rotated smoothly). After the lift adjustment the current had decreased approx 2A to 88A, 89A, 92A (still 490V, still 130 psig/525gpm).
We varied flow by pumping to bypass. We confirmed that for any discharge pressure higher or lower than 130A, the current readings went down (this is in agreement with the shape of the BHP curve).
We cannot precisely determine the head of the pump since the suction pressure (far underground is unknown), but we believe the flow info is sufficient to locate us on the curve. We are perplexed that the motor can deliver more current than the pump appears capable of consuming on paper.
I don't think it is a problem with the motor itself since the motor has been replaced and the previous motor had similar high current draw. In fact this motor has been replaced about 3 times in last 10 years for various reasons I am not totally familiar with. It is a tough outdoor environment. With 1.15sf it should be able to withstand this level of overload but I would like to try to understand it better.
Any suggestions what might be going on or how to troubleshoot?